xmlns:atom="http://www.w3.org/2005/Atom"

PART FConservation of fuel and power

Deemed-to-satisfy provisions for regulations F2, F3 and F4

F5—(1) The requirements of regulation F2 shall be deemed to be satisfied, in the case of a building specified in column (2) of Table F opposite the reference to that regulation, if the fabric of the building is designed and constructed in accordance with the relevant provisions of the publications specified opposite thereto in column (3), as amended by the publications specified opposite thereto in column (4).

(2) The requirements of regulation F3 shall be deemed to be satisfied, in the case of a building specified in column (2) of Table F opposite the reference to that regulation, if

(a)the space heating and hot water supply system used in the building is provided with controls in accordance with the relevant provisions of the publications specified opposite thereto in column (3), as amended by the publications specified opposite thereto in column (4); and

(b)the artificial lighting system used in the building is designed and constructed in accordance with the relevant provisions of the publications specified opposite thereto in column (3), as amended by the publications specified opposite thereto in column (4).

(3) The requirements of regulation F4 shall be deemed to be satisfied, in the case of a building specified in column (2) of Table F opposite the reference to that regulation, if the pipes, ducts and hot water storage vessels used in the building are insulated in accordance with the relevant provisions of the publications specified opposite thereto in column (3), as amended by the publications opposite thereto in column (4).